I have issue with my MTP1500 Siemens Unified HMI. It does not connect to PLC, but when I use
WinCC unified Runtime then it works fine. I noticed that error on the screen says that Certificate is not valid?
Do I need certificate? I tried to add it but that does not change anything.
Using TIA Portal V19
I think this is an issue with the Current time set on HMI, which may be different from PLC time. Set the HMI time the same as the PLC - HMI connection should work.
This is quite a common issue with Unified panels and new certificate-based connections.